Default ONAN 6500 NH spec K

Generator runs fine except under load (A/C or Air Compressor) shut's off. Replaced 300-3763 board no change. Removed gear case inspected governor ( 9 balls not 10) checked specs according to manual OK. Removed oil pan found fiber type washer broken in half can't find ware washer goes. Called Onan repairman (3) no call back ? Any help would be appreciated. Thanks Bobby.
Bobby4080 is offline   Reply With Quote
Old 12-07-2015, 05:32 PM   #2
voltdr
Senior Member
 
Join Date: Jan 2008
Location: Texas
Posts: 706
Likes: 77
Liked 100 Times in 51 Posts
Default Re: ONAN 6500 NH spec K

A few years ago I had an NMH (I think) that did the same thing. Had a guy put in new rings and valves. Then it ran fine under full load. Motor was just down on power to pull the generator load of anything more than lights, etc.
Dan
voltdr is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 04:51 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.
Copyright Class Racer.com. All Rights Reserved. Designated trademarks and brands are the property of their respective owners.