Just a follow up on my problems with an Onan 10K generator.

The generator would run for around 30 minutes and shut down. Code was always 36. We checked fuel flow and fuel pump power which was fine. Finally I shook the E1 fuel pump wire on the circuit board connector and it shut off. Checked connector and it was good. Checked the board connections and they were tight.

What is happening is the vibration from the generator is causing a connection issue on the board. Needs a board but they are $800.

So I decided to wire around the fuel pump circuit and put a separate wire to power the pump. If I had more time I would have wired it into the relays already inside the sheet metal but it appears everything is run off grounding not positive signal.

Here is what I did, put a small switch on the dash next to the generator start switch. Pulled power from the lighter circuit and put another fuse in line. Ran the wire down to the generator and connected to the fuel pump wire. So when I start the generator I also flip the switch on the fuel pump circuit. Now runs all day no more problems. Total amount the fix was $15.

When you shut off the generator you just flip the fuel pump circuit off also. Even if you don't it will still shut off.
__________________
Don Higgins - Super Comp #360H
Don Higgins is offline   Reply With Quote
Old 03-02-2014, 09:18 PM   #2
Rich Biebel
VIP Member
 
Rich Biebel's Avatar
 
Join Date: Jun 2007
Location: Northern New Jersey suburbs
Posts: 2,314
Likes: 25
Liked 544 Times in 213 Posts
Default Re: Generator Questions and Answers, by R&J Control Inc

Don the fuel pump power circuit on many Onan PC boards has this same problem. I have replaced countless A-1 controllers as that is what Onan calls them.

They routinely run for some time and than shutdown.....and may or may not restart. Diesels as well as gas engine units.

Your solution is fine....but obviously you have to remember to shut off the pump switch.

Sometimes the pin connections are the problem but more often it is internal to the PC board....heat seems to be the problem....The hotter it is out the more likely they are to fail.....
__________________
Rich Biebel
S/C 1479
Stock 147R
Rich Biebel is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 02:24 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.
Copyright Class Racer.com. All Rights Reserved. Designated trademarks and brands are the property of their respective owners.