Rich,I have an onan generator in my motorhome,I pulled the aux. battery to charge it over the winter. I just put it in and it has one lead to neg. side of battery and two leads to positive side . Cleaned all connections and started it . Unit runs fine,but NO electric power for said unit. I did check all fuses and breakers all seem and look good.Numbers on unit model etc. are 4kyfa26100b. Any suggestions as to the problem switches I might have over looked? Trying to make Div#1 points meet at Maple Grove this is my 1st time our this season. Oh my!!!!! Thanks in advance, I am done with Camping Would Service with this unit,no Onan Tech on site its sent out so you can't talk to a tech at all. Paul D. Ladd A100 P/SA 1965 Chevelle Wagon Red and White, "Call the Wagon" home phone is 1-856-848-7237 if you would like to call. P.S. Are you going to the Grove???
STONE BROKE RACING is offline   Reply With Quote
Old 05-20-2019, 12:25 PM   #2
Rich Biebel
VIP Member
 
Rich Biebel's Avatar
 
Join Date: Jun 2007
Location: Northern New Jersey suburbs
Posts: 2,273
Likes: 25
Liked 510 Times in 200 Posts
Default Re: Rich Biebel

Most Onan's will not stay running if it is not producing AC voltage.

They also will not stay running without a battery connected to them.

There is an AC breaker at the machine itself.....near the start stop switch....below or on the side of the rocker switch.

Start there....is it on ?

Next would be to try and find a place to check for AC output voltage as close to the machine as possible. Maybe a connection box is accessible near the machine.

You need to verify if the problem is the generator itself or a connection issue down stream from the generator....

If the generator is running and has no AC output downstream, I would get at the back of the breaker....

There is a plastic cover behind the breaker and the panel is removable...

I have seen those breakers go bad but usually not like this.

Don't assume there is no voltage there with it running......Electricity can kill you...…..

I wear rubber gloves a lot just for the added protection.....be safe testing it....

Yes I will be at MG and usually park along the tree line in the big field.....

If you cant find the trouble I am sure I can find some time to take a look for you....
__________________
Rich Biebel
S/C 1479
Rich Biebel is offline   Reply With Quote
Old 05-20-2019, 02:52 PM   #3
STONE BROKE RACING
Junior Member
 
Join Date: Sep 2009
Posts: 9
Likes: 0
Liked 0 Times in 0 Posts
Default Re: Rich Biebel

Rich,thank you for reply, yes the breaker is on and I did turn it off and on twice. Still nothing and as my ref. I use the clock for microwave to see if its got power. I have my motorhome and trailer at a storage area as no room at my home,at48ft total,well you know!!!!! Electric and I really don't mesh so not to have to many hands in soup,I'll just come up and if you have time to look at the unit that will be excellent. I do park in that same field accross from Sunoco Fuel Station their at the track. Bob Bender is a good friend of mine so I may be parked by him also. Look forward to seeing and meeting you. Beer Coors Lite served also along with cash for your services,thank you. Paul D.Ladd A100 Stock P/SA
STONE BROKE RACING is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 06:17 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Copyright © Class Racer.com. All Rights Reserved. Designated trademarks and brands are the property of their respective owners.